Hello folks,
Thinking about BS guidance for separation distances for EMC.
BS EN 50174-2:2018 gives a nice formula for working out distances between power supplies /control cable, with criteria to be met.
BS 7671 Table A444.1 gives some minimum values which I'm Ok with, as I can arrive at the same values using the criteria and formula from BS EN 50174-2:2018.
however BS7671 goes on to state that if the criteria for Table A444.1 cannot be met then Table A444.2 should be used. I find Table A444.2 more problematic as I cannot understand where the values were derived from, and it means I can't use the formula in 50147 for anything over 600A , or IT application unknown, when actually 50174 allows for both those scenarios.
What is the source material for Table 444.2?
Why does it use obsolete nominal voltages 240 and 415V?
Why does it consider voltages (the left side of the table) for separation when EMC is current driven?
Is the 600A mentioned three phase or single phase?
Many thanks for anyone taking the time to humour me and my ruminations.
Ben