On conducting a condition report the rf was found to be wired in 3/036 on a b16 mcb.
Have calculated the csa of the live conductors to be about 1.9mm2.Subject to circuit
length,could I convert to 2 radials and use the OSG table for 1.5mm cable on a 16A
mcb?The circuit serves a small lounge and bedroom.Otherwise,suspect this would attract
a C2 code.
Thanks for any advice,Hz