Standard DNO Fault Current - incompatible MCB rating

Hi , I have a question.....  A small office building requires a new distribution board local to a 100A TPN DNO cut-out however, in lieu of an existing EICR, the standard Prospective line fault current is 25kA (3 phase), 16kA (1 phase).  With the DB in close proximity to the DNO the OCPD for final circuits needs to be types ITRO of 25kA breaking capacity ...... which are not available.... How would you mitigate this risk?

Am I missing something...?

Parents
  • Am I missing something...?

    Yep - backup protection - as broadgage says - see reg 536.4.201 - just about any UK consumer unit will be rated at 16kA overall regardless of the breaking capacity of individual MCBs - courtesy of annexe ZB of BS EN 61439-3.

    For other types of distribution board the same principle of using an upstream device for backup protection can also apply - see 2nd paragraph of 434.5.1 - usually DB manufacturers provide data about the rating and types of suitable upstream devices.

       - Andy.

  • Thanks Andy, 434.5.1 answers it perfectly! I was including a fuse switch disconnector with BS-88 fuses upstream of the DB which could have given me selectivity issues with the CUT-OUT fuses however I'll put an electronic 36kA MCCB instead and that will resolve my problem.

    Thanks all for your input!

Reply
  • Thanks Andy, 434.5.1 answers it perfectly! I was including a fuse switch disconnector with BS-88 fuses upstream of the DB which could have given me selectivity issues with the CUT-OUT fuses however I'll put an electronic 36kA MCCB instead and that will resolve my problem.

    Thanks all for your input!

Children
  • I was including a fuse switch disconnector with BS-88 fuses upstream of the DB which could have given me selectivity issues with the CUT-OUT fuses however I'll put an electronic 36kA MCCB instead and that will resolve my problem.

    If you blow either one or two 100 A fuses, I think that selectivity is the least of your problems!