Standard DNO Fault Current - incompatible MCB rating

Hi , I have a question.....  A small office building requires a new distribution board local to a 100A TPN DNO cut-out however, in lieu of an existing EICR, the standard Prospective line fault current is 25kA (3 phase), 16kA (1 phase).  With the DB in close proximity to the DNO the OCPD for final circuits needs to be types ITRO of 25kA breaking capacity ...... which are not available.... How would you mitigate this risk?

Am I missing something...?

Parents
  • Use the function in Amtech for has upstream protection which will show you what the PFC is at a particular part of the installation.

Reply
  • Use the function in Amtech for has upstream protection which will show you what the PFC is at a particular part of the installation.