Standard DNO Fault Current - incompatible MCB rating

Hi , I have a question.....  A small office building requires a new distribution board local to a 100A TPN DNO cut-out however, in lieu of an existing EICR, the standard Prospective line fault current is 25kA (3 phase), 16kA (1 phase).  With the DB in close proximity to the DNO the OCPD for final circuits needs to be types ITRO of 25kA breaking capacity ...... which are not available.... How would you mitigate this risk?

Am I missing something...?

Parents
  • BTW, the highest prospective fault current that I have have found at a 13 amp socket outlet. was about 20 Ka not actually in the substation, but immediately adjacent.

    400 amp circuit from substation, into customers main switchgear, this supplied sub-mains to different areas of the building, and a small fuseboard adjacent. Socket outlet on side of fuseboard.

Reply
  • BTW, the highest prospective fault current that I have have found at a 13 amp socket outlet. was about 20 Ka not actually in the substation, but immediately adjacent.

    400 amp circuit from substation, into customers main switchgear, this supplied sub-mains to different areas of the building, and a small fuseboard adjacent. Socket outlet on side of fuseboard.

Children
  • I just love BS88-3 (IEC ASTA certified. 60269-3) fuses. Rated at 80kA. Totally reliable and they can reliably disconnect within just one half cycle. Also the wee grains of sand quash the arc. A wonder to behold. And when they blow a new factory fresh one is installed. Again totally reliable, unused, unharmed and wonderful.

    Z.