Standard DNO Fault Current - incompatible MCB rating

Hi , I have a question.....  A small office building requires a new distribution board local to a 100A TPN DNO cut-out however, in lieu of an existing EICR, the standard Prospective line fault current is 25kA (3 phase), 16kA (1 phase).  With the DB in close proximity to the DNO the OCPD for final circuits needs to be types ITRO of 25kA breaking capacity ...... which are not available.... How would you mitigate this risk?

Am I missing something...?

Parents
  • Neal

    If you have Amtech then model the installation from the transformer terminals using the transformer data. The layers of circuit protection will have a current limiting effect along with the cable CSA and lengths. Then look at the actual fault current at the DB. 

    JP

  • Thanks John, good idea..

    What I have done is set the worst case DNO supply characteristics as being at the Transformer and then modelled the cable to the distribution board... Line fault current now drops below the 16kA MCB rating.. 

    This identifies to me that it is highly unlikely that there will be a line fault current of 25kA magnitude unless installing a distribution board in a sub-station!!  Therefore is rarely an issue. But I'm pleased to have gone through the process and come to this conclusion.

    Thanks all for your help.

  • What I have done is set the worst case DNO supply characteristics as being at the Transformer and then modelled the cable to the distribution board... Line fault current now drops below the 16kA MCB rating.

    Splendid! But surely the situation is not so complicated that specialised software is required?

    Concerning proximity to a substation (be it the DNO's or a private one), I'd be most interested to know the Ze of our neighbour across the road right next door to the transformer, but I have never had the cheek to ask to measure it. Doubtless the main goes out into the street, along a few yards, and then back in as the service cable, so a U-shaped route, albeit a short 'un.

Reply
  • What I have done is set the worst case DNO supply characteristics as being at the Transformer and then modelled the cable to the distribution board... Line fault current now drops below the 16kA MCB rating.

    Splendid! But surely the situation is not so complicated that specialised software is required?

    Concerning proximity to a substation (be it the DNO's or a private one), I'd be most interested to know the Ze of our neighbour across the road right next door to the transformer, but I have never had the cheek to ask to measure it. Doubtless the main goes out into the street, along a few yards, and then back in as the service cable, so a U-shaped route, albeit a short 'un.