The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Electrical Equipment in Proximity to Sprinklers - BS7671 Reg 512.2

Hello,

A contractor is proposing to install IP20 luminaires below the sprinkler heads in a new build industrial facility.  If the sprinklers go off (which can be at a relatively low temperature of 60 degrees Celsius)) then the luminaires will be subject to water ingress and could become waterlogged. 

I have asked them to comment on how this complies with BS7671 regulation 512.2 (specifically 512.2.1).  The answer they have provided is vague and to the effect that "this is the way we've always done it".  They haven't provided a specific answer as to how this complies with BS7671.

I am trying to understand how the wiring regulations should be applied where we have sprinklers in buildings:  I am struggling to imagine that electrical installations throughout buildings are IP rated for the sprinkler system activation.

Does anyone have experience in answering this question?

Thanks,

Richard

Parents
  • Also a fair chance that the light fittings may be combined and contain emergency lighting capability. If there is a fire and the sprinklers are going to operate then you are going to want the ELs to operate if the fire causes a loss of power.

    JP

Reply
  • Also a fair chance that the light fittings may be combined and contain emergency lighting capability. If there is a fire and the sprinklers are going to operate then you are going to want the ELs to operate if the fire causes a loss of power.

    JP

Children
No Data