Replace Ceramic Hob with Induction Hob Query [UK]

Existing installation over a decade old:

  • Ceramic Hob
  • Fed from 32A 2 pole Isolator
  • Hob has dedicated Radial Circuit 32A MCB (note for avoidance of doubt: oven is on Separate 32A MCB radial circuit)
  • Hob Radial Circuyt has 6mm2 cable (confirmed from elec cert).

Existing hob is woking fine but considering replacing with induction hob for energy efficiency reasons.

So, Question; If it is replaced with an new induction hob (like for like other than change from ceramic radiant hob to induction hob):

1) is it mandatory for the swapout (disconnection of cable connection to old and reconnection to new) to be undertaken by a qualified electrician?

2) Will replacement of ceramic hob with induction hob mean installation of RCD protection of the circuit will be required (eg change from MCB to RCBO [obviously] by qualified electrician)?

Thanks,

Paul

Parents
  • an altered such circuit would also  require an RCD wheb altered

    Not necessarily - new work should comply with current regs, but there's no stipulation that an entire circuit needs to be brought up to date when working on part of it.

       - Andy.

Reply
  • an altered such circuit would also  require an RCD wheb altered

    Not necessarily - new work should comply with current regs, but there's no stipulation that an entire circuit needs to be brought up to date when working on part of it.

       - Andy.