This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Building regulations on vertical chase to the masonry for meter tail installation

Hi , I need to find out what is the legal requirement for vertical chases to the masonry wall for meter tail installation?

Parents
  • Is this from the point of view of the structure: e.g. not too deep; or from the electricians view: e.g. cables buried deep enough to not require mechanical or RCD protection?

Reply
  • Is this from the point of view of the structure: e.g. not too deep; or from the electricians view: e.g. cables buried deep enough to not require mechanical or RCD protection?

Children
  • to meet both you may find you need a considerably thicker wall !  You can usually cut up to 33% into a load bearing wall without seriously weakening it and a lot less for horizontal cuts, -but  is it load bearing ? not all are, 
    On the other hand the wiring regs assume the hazard is  50mm long screws and nails and require the cable to be deeper than that from the final surface, or the route to be visible, or conduit/trunking etc or to be in a corner.
    Mike.

  • Yes, in general with cable installation without compromising structure

  • Its the wall, between external wall and plasterboard . The wall are thermalise breeze block I think.