MK SPD Device in a RCBO CU - puts main isolator in 2nd place. - Chinese or what ?

MK have given me a schematic to enable an RCBO only Consumer Unit on MK Sentry 

This puts the main isolation physically (not electrically) after the SPD.  Any experience of this on MK please ? Seems clumsy ?

Parents
  • That's a pretty standard arrangement. Although I'd note that Wylex now do a single-width SPD with built-in fusible-link OCPD which has the L connection on the base, so it can sit directly on the bus bar.

Reply
  • That's a pretty standard arrangement. Although I'd note that Wylex now do a single-width SPD with built-in fusible-link OCPD which has the L connection on the base, so it can sit directly on the bus bar.