When did type A RCD's become a requirement for EV chargers

I am just looking at a potential EV charger installation for a house that has supposedly been prewired for an E charger but it's protected by a type AC RCCB. Then to make things worse it's in an easy 9 consumer unit and the only type A RCCB they have is only rated at 63A, the ev charger is sharing the RCCB with two other 32A circuits plus 4 others. I don't have any space for extra devices and will need to put an extra consumer unit in.

I am wondering if the install ever complied with the regulations. Looking at regulation 722.531.2.101 it's in the first 18th edition but i don't know if ev charging was even in any of the 17th editions?

Also quite shocking that I can't get a 100A type A RCCB from Schneider for the easy 9. 

Parents
  • My own supply, which is looped, was down rated from 100 amps over ten years ago, which doesn’t worry me at the moment.

    I bought a data logger and tried it out at home, it doesn’t record below 10 amps so didn’t record much at all, over a fortnight it peaked very briefly at 32 amps, so I would not worry about installing an EV charger at home without altering anything.

Reply
  • My own supply, which is looped, was down rated from 100 amps over ten years ago, which doesn’t worry me at the moment.

    I bought a data logger and tried it out at home, it doesn’t record below 10 amps so didn’t record much at all, over a fortnight it peaked very briefly at 32 amps, so I would not worry about installing an EV charger at home without altering anything.