461.2

If an external high level air-con unit has a rotary isolator positioned next to it, is it good practice to wire the isolator so that it disconnects both L. and N. of the supply?

Z.

Parents
  • (b) possibly will be maintained by someone who may be accessing from outside the building (i.e. outside the influence of the main bonding) - and the risk of a potential difference between N and Earth (rather than PE / MET) is greater. The risk is

    So on TN, especially PME, systems, if we're isolating the N, should we be isolating the PE conductor too?

       - Andy.

  • plug and socket then if you want that, nothing like a 3ft contact gap.

    Mike

Reply
  • plug and socket then if you want that, nothing like a 3ft contact gap.

    Mike