This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

MCCB Max ZS & Correction factor for temperature rise under fault.

Hello All,

I have recently completed an EICR which has MCCB's fitted most are Merlin Gerin NS with TM D or STR blocks all feeding large final or submains, allowing for a 5s dis connection time although the data tables the zs is the same for 0.4 or 5s. I have calculated the max Zs values for these taking into account the tolerance permitted by Schneider and the C min value. I have used these as the Max Zs recorded on the test sheet. However when coding I have taken 80% of this value in lieu of the possible temperature rise under fault conditions. The client has since queried this as it has caused some circuits to fail. When I spoke to Schneider they said as I have there maximum Zs values from there tables these can be used (which are the same as what I calculated on site) but there calculation are done at ambient of 30 degrees. Therefore I believe a derating factor would still need to be applied to allow for the possible temperature rise in the conductors under fault condition. And that where the measured Zs does not meet this corrected max Zs a C2 would be the correct coding.  

Look forward to hearing your opinions. 

Thank you

Parents
  • Also note that a Zs on a running system may already have a hot live and a cool earth so keep your wits about you about the true test conditions.

    Good point. Similarly not so long ago the appendix said we need only apply the adjustment factor to the installation's conductors (R1+R2) and could use the external (Ze) part as measured - that option seems to have disappeared, but still appendix 3 is still only "Informative" and 'other methods are not precluded', so something along those lines could still be appropriate.

       - Andy.

Reply
  • Also note that a Zs on a running system may already have a hot live and a cool earth so keep your wits about you about the true test conditions.

    Good point. Similarly not so long ago the appendix said we need only apply the adjustment factor to the installation's conductors (R1+R2) and could use the external (Ze) part as measured - that option seems to have disappeared, but still appendix 3 is still only "Informative" and 'other methods are not precluded', so something along those lines could still be appropriate.

       - Andy.

Children
No Data