Eaton Glasgow Screw Torque

Hi all,

Just installing a glasgow 104gc switch disconnector. Instructions state 10Nm for terminals, so get torquing and the first screw breaks! As this is a TP+SN unit there is no netural bar but the instructions state 3Nm for neutral, so torque all other terminals to 3Nm and no problem!

Phoned Eaton technical and they insist that the terminals should be 10Nm - which for a small tinned brass flat head screw seems excessive! All the Schneider gear using similiar terminals I have fitted seems to be 3.5Nm and they have a far better combination pozi head.

Anyway, would appreciate some thoughts on this. I must admit I'm happy with 3Nm on the terminals but the regs say to follow the manufactures guidance....

Thanks

Parents Reply
  • I think the only people who can answer this are Eaton themselves.

    Have you discussed the breakage with them?

Children
  • I have yes, they insisted on 10Nm but the tech i spoke to seemed to be just quoting the pdf you have linked to.. I guess it begs the question of how close you should follow the manufactures advice when in the real world it seems incorrect..