Cables in ducts underground
Good morning
I always thought that if you are installing cables underground (e.g. for external lighting, Vehicles Chargers, submains to another building etc) you always use SWA cables because this offers mechanical protection.
Is this coming from a specific regulation though?
Because I have someone saying I could use double insulated cables in the underground ducts if its a short run.
However this feels odd.
Is there any regulation that I can refer to?
Sorry for the ignorance
Cheers
  • Regulation 522.8.10. Cables buried in the ground have to be armoured, or be installed in underground conduits or ducts offering 'equivalent mechanical protection'.
    Unarmoured cables in 750N dual-walled ducts ('twin wall') to BS EN 61386-24 should be OK ... BUT you need to make sure:
    • water can't build up in there, as most cables (even XLPE SWA) are not submersible;
    • ends are suitably sealed against rodents, rabbits etc.
  • Hi Apostolos, here is a similar topic from the archive of the previous forum:
    https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=62576
  • Some more from the archive:
    engx.theiet.org/.../why-steel-in-swa
  • Unarmoured cables in 750N dual-walled ducts ('twin wall') to BS EN 61386-24 should be OK
    It does depend on the situation though - I reckon twinwall wouldn't prevent penetration by a simple garden fork - so I wouldn't want want to rely on it say if shallow buried in garden for example. In more controlled or benign environments it might be fine though.
    The big advantage of SWA etc is not so much the mechanical protection provided by the armour (a garden fork can pierce that relatively easily too)  - but the fact that the armour is Earthed - so anything conductive (digging tool, JCB bucket, tent peg or whatever) that penetrates through to a live core will almost certainly cause a short to the armour and so trigger automatic disconnection of supply. Same with concentric DNO cables where the concentric outer conductor is relatively soft copper rather than steel - it's the Earthing rather than mechanical protection that's relied on.