Earthing system

Recently mobile welfare cabins with integral generators were used on site.

Test sheets supplied gave the earthing system as IT. 

2 phase 3 wire

NO earth electrode was used when the suppliers tested before arrival on site.

On arrival on site an earth electrode was installed and the cabin was connected to this.

Is the cabin now a TT system?

Parents
  • It won't be TT unless there are two separate electrodes - one for the source (generator) and another for the consumer.

    The usual arrangement for generators is TN-S with the local electrode serving as the source electrode (like the one that's at the substation in a public supply), or for small systems (e.g. <3kVA) a separated system is sometimes used (neither the source nor exposed parts of the installation deliberately connected to an Earth electrode).

    IT is a possibility - especially if someone has connected the installation's exposed-conductive-parts to the electrode without creating a N-PE link. Whether that's the best choice is another matter (IT systems are usually chosen where resilience on first faults is needed - and normally include insulation monitors and warning systems).

       - Andy.

Reply
  • It won't be TT unless there are two separate electrodes - one for the source (generator) and another for the consumer.

    The usual arrangement for generators is TN-S with the local electrode serving as the source electrode (like the one that's at the substation in a public supply), or for small systems (e.g. <3kVA) a separated system is sometimes used (neither the source nor exposed parts of the installation deliberately connected to an Earth electrode).

    IT is a possibility - especially if someone has connected the installation's exposed-conductive-parts to the electrode without creating a N-PE link. Whether that's the best choice is another matter (IT systems are usually chosen where resilience on first faults is needed - and normally include insulation monitors and warning systems).

       - Andy.