Very low Ra reading disappears when connected back up.

Hi Guys

I had some very strange readings today when doing an EICR.   Property is a semi detached cottage in a very rural location. Over head supply. 

The first thing i noticed when i arrived was a piece of angle iron driven into the ground outside the front door with a corroded 10mm earth cable bolted to it exposed for all to see.

The consumer unit is located just inside the front door in a cupboard and i can see the earth cable going out through the door frame.  I disconnected it at the CU and got an Ra reading of just over 2 ohms so i am obviously amazed. I reconnect it to the CU to get a PFC reading etc and the Zdb is nearly 300ohms with the original earth reconnected. I disconnected it again and got just over 2 ohms again. Reconnected it and got around 300ohms.  

This is a new one on me, does anyone know what could be going on ?

Cheers  Gary

Parents
  • Thank you for the replies.  I didn't think to do a 2 wire test, I have a newish tester to me (KT66DL) which does have that function.   I have coded it as a C2 for now ( absence of a reliable and effective means of earthing)  along with a few others so no doubt will have to go back there at some point.

    Gary