Floating Neutral with Single Phase Inverters in machinery

Hi, As a new member I thought I would throw out my first question from a recent experience. 

I had a customer who bought a machine which had Single phase supplied servo motors & a Single phase Supplied Inverter. Each Servo drive was supplied by a phase

Servo 1 - L1 - N

Servo 2 - L2 - N

Servo 3 - L3 - N 

Inverter L Something to N.

These where protected by Type C MCBs in the control cabinet. The machine had a 3Pole Isolator only isolating the Phases. 

ISSUE.

The Electrician had wired a new 32a 5 Pin Plug to supply the machine. Upon commissioning the machine our engineer had done a voltage check & phase rotation check at the supply coming into the machine which. had tested     230v  L1-N, L2-N L3-N.    400 v L1-L2.   L1-L3.  L2-L3.       230v  L1-E, L2-E L3-E

As far as the engineer was concerned the correct voltages tested out ok and the next step was to turn on the machine. 

Big Puff of smoke which took out the cooling fan, 24v PSU & single phase inverter. 

When we looked into the issue, it turned out the electrician had not wires the neutral in the distribution board assuming they only needed 3 Phase. Checking the voltage between Line & Neutral gave us almost 400v when the machine was on. It appears the voltage supplying the Servo Drives had no where for the current to go with the disconnected neutral and created a potential through the neutral providing all the single phase devices with 400V. However when the machine was switched off, the neutral was not switched and a return path must of been created through the drives or PSU to Ground. 

Question

What are the regulations on protecting single phase drives with using more than 1 phase in the same cabinet & what devices should be used to protect against this from happening?

Thanks

Symon 

Parents
  • In my view, installing a FIVE PIN Ceeform outlet without a neutral is simply wrong. May not be specifically prohibited by regulations, but what about common sense, or accepted practice ? It is nearly as bad as fitting a 13 amp socket without an earth because only double insulated appliances are to be used.

    If no neutral is required then the four pin type should be installed.

  • And, the installer of the machine should have read the manufacturer's installation requirements for the machine, and also noted the machine terminal markings and supply needs. Was there a neutral terminal in the main terminal box? We may all have been fooled by the lack of Neutral at the supply socket if it had an apparent  Neutral provision, and the supply Voltages seemed good. Testing at the machine with a neon Voltage tester or a sensitive digital multi meter may have not revealed the true picture. A tungsten test lamp or a small load may have revealed the lack of a Neutral as Mike has detailed above. An artificial internal Neutral may have been created by internal filters or other components.

    Z.

  • This was my point exactly, and the shear laziness of not connecting one core which was just coiled up is beyond belief. If there is five pins, there is five wires. No excuses on this one. If we didn’t require the N it would of been left out on the plug side. Not the socket side. 

    thanks

    sy 

  • The installer of the machine was fooled.

    the responsibility of supply is down to the electrician. A five pin socket was installed for the machine by an electrician. 

    the machine was plugged in, when tested all the voltages was fooled as we had a 230V reading from L1- N L2-N L3-N 

    His job was to commission the machine. Not install the supply. It must of been created through a device to E somewhere, then when powered up through the phases !!!

    Sy 

Reply
  • The installer of the machine was fooled.

    the responsibility of supply is down to the electrician. A five pin socket was installed for the machine by an electrician. 

    the machine was plugged in, when tested all the voltages was fooled as we had a 230V reading from L1- N L2-N L3-N 

    His job was to commission the machine. Not install the supply. It must of been created through a device to E somewhere, then when powered up through the phases !!!

    Sy 