Floating Neutral with Single Phase Inverters in machinery

Hi, As a new member I thought I would throw out my first question from a recent experience. 

I had a customer who bought a machine which had Single phase supplied servo motors & a Single phase Supplied Inverter. Each Servo drive was supplied by a phase

Servo 1 - L1 - N

Servo 2 - L2 - N

Servo 3 - L3 - N 

Inverter L Something to N.

These where protected by Type C MCBs in the control cabinet. The machine had a 3Pole Isolator only isolating the Phases. 

ISSUE.

The Electrician had wired a new 32a 5 Pin Plug to supply the machine. Upon commissioning the machine our engineer had done a voltage check & phase rotation check at the supply coming into the machine which. had tested     230v  L1-N, L2-N L3-N.    400 v L1-L2.   L1-L3.  L2-L3.       230v  L1-E, L2-E L3-E

As far as the engineer was concerned the correct voltages tested out ok and the next step was to turn on the machine. 

Big Puff of smoke which took out the cooling fan, 24v PSU & single phase inverter. 

When we looked into the issue, it turned out the electrician had not wires the neutral in the distribution board assuming they only needed 3 Phase. Checking the voltage between Line & Neutral gave us almost 400v when the machine was on. It appears the voltage supplying the Servo Drives had no where for the current to go with the disconnected neutral and created a potential through the neutral providing all the single phase devices with 400V. However when the machine was switched off, the neutral was not switched and a return path must of been created through the drives or PSU to Ground. 

Question

What are the regulations on protecting single phase drives with using more than 1 phase in the same cabinet & what devices should be used to protect against this from happening?

Thanks

Symon 

Parents
  • In my view very little, if indeed any blame should attach to the person installing and commissioning the machine. They should of course read the instructions, and these instructions probably included checking for correct phase rotation and voltages are as expected. In the absence of any such instructions, then such checks are still good practice.

    It is not in my view the job of the installer to go beyond phase rotation and voltage checks. Neither should they be expected to check the cable size for example. 

    There have to be some assumptions made that the electrician installing outlet did the job properly, including use of the correct size and type of cable, correct earthing, and connecting the neutral. 

Reply
  • In my view very little, if indeed any blame should attach to the person installing and commissioning the machine. They should of course read the instructions, and these instructions probably included checking for correct phase rotation and voltages are as expected. In the absence of any such instructions, then such checks are still good practice.

    It is not in my view the job of the installer to go beyond phase rotation and voltage checks. Neither should they be expected to check the cable size for example. 

    There have to be some assumptions made that the electrician installing outlet did the job properly, including use of the correct size and type of cable, correct earthing, and connecting the neutral. 

Children
  • Hi Broadgage, Thanks for your reply.

    I agree with there has to be assumptions made, however the relevant checks where still performed by the commissioning person from the cabinet side. 

    The person installing the machine did the relevant checks at the machine side, which is what he was responsible for. The fact that he had 230v from L1-N and so on before powering up the machine and 400v P-P and correct rotation at the DIN terminals there would in my opinion no need to go further. There where no continuity between E + N either with the machine UNPLUGGED which again confused matters. 

    This forum was just to shed some light on how the N can appear with the equipment used as to prevent this ever happening again. Maybe we do use some small load between L-N with the N disconnected completely from devices inside the cabinet in the future. That would be the only way to check a functional N. 

    It was just a little disappointing that the electrician who had installed a 5 core cable, 5 pin plug and not connected the N. I know he is not obliged but I have to agree with what you said earlier. Doesn't seem practical to anyone. 

     Thanks 

    Sy 

  • Also just to mention, we are not really looking to blame people, we have all accepted what's happened, Just how these things happen & how to look out for them in the future.

  • A three phase supply with unbalanced loads and the neutral disconnected.

    It is best not to try this at home.

    Neutral Fault (three phase) - YouTube

    Z.