Any requirements to have pressure test 3.5KV 1 min on 600/1000V BS 6724 cable in field?

I know the similar requirements for LV cable manufacturers and LV switchboard in field. But never heard to test on new installed cable. 
Is there any risk to have breakdown?

Parents
  • no harm to have such test

    As I recall, for some appliances a 3.5kV test is used at manufacture stage, but is NOT recommended for in-service testing, since the higher voltage can stress the insulation to the point of risking permanent damage if it's repeated too often. 500V is far more usual for on-site testing. I'd suspect there may be a similar argument for cables - but others here will have better definite knowledge.

           - Andy.

  • thank you Andy