This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Three Phase Generator.

A local man is disconnecting from the grid due to rising costs. He has bought an AG-50 50kVA three phase diesel generator. The maker is Fuj[an Yihua Electrical Machinery Co. Ltd. The generator will be used for electric showers and a washing machine on a camping site. What advice can you provide for me so that all goes well with the installation. The certificate of conformity states 380 Volt, p.f. 0.8, 76 Amp. 50Hz.

Is foundation earthing a good idea whilst the concrete slab is being made?

Thanks,

Z.

Parents
  • How many electric showers ? Might only be three from that size generator. 50 KVA at 0.8 p.f. is about 40 kw. 13 kw per phase=one shower per phase plus a margin for other loads.

Reply
  • How many electric showers ? Might only be three from that size generator. 50 KVA at 0.8 p.f. is about 40 kw. 13 kw per phase=one shower per phase plus a margin for other loads.

Children
No Data