Bonding in greenhouse

On an eicr

I have a greenhouse connected to a sub DB in an outhouse, which is on a TT earth. Circuit is protected by upstream 30mA and 100mA RCD's.

I am debating in my mind if the frame of the greenhouse should be bonded to the single socket in the green house.

I would consider the frame as an extraneous part and therefore first reaction is to bond it.

But then thinking about it. bonding would reduce the risk of shock inside the greenhouse in the case of the socket became live but increase the risk of shock outside the greenhouse if the socket and greenhouse became live.

On balance I am tempted to go with not bonding, what are your thoughts?

Parents
  • What do you mean by this statement please?

    "But then thinking about it. bonding would reduce the risk of shock inside the greenhouse in the case of the socket became live but increase the risk of shock outside the greenhouse if the socket and greenhouse became live."

    The socket became live???????? The socket is best being a plastic weatherproof type to keep water out.

    Z.

Reply
  • What do you mean by this statement please?

    "But then thinking about it. bonding would reduce the risk of shock inside the greenhouse in the case of the socket became live but increase the risk of shock outside the greenhouse if the socket and greenhouse became live."

    The socket became live???????? The socket is best being a plastic weatherproof type to keep water out.

    Z.

Children
  • Sorry not very clear. I am thinking worst case scenario is case of metal clad socket becomes live along with cpc connections. Could happen if there is a short to earth and RCD fails to operate.

    Then if the socket is bonded to the greenhouse there would be minimal Potential difference between the socket and green house frame but someone outside the greenhouse is at risk because there could be a significant potential difference between the green house frame and earth.

    If the greenhouse has a very low resistance to earth, lets say 20 ohms then bonding makes sense but much above that, if the RCD fails there is a real potential for a fault to create a dangerous voltage.

  • "Sorry not very clear. I am thinking worst case scenario is case of metal clad socket becomes live along with cpc connections. Could happen if there is a short to earth and RCD fails to operate."

    There are two R.C.D.s connected in series. The chance of both failing is very slim indeed.

    Z.