Bonding in greenhouse

On an eicr

I have a greenhouse connected to a sub DB in an outhouse, which is on a TT earth. Circuit is protected by upstream 30mA and 100mA RCD's.

I am debating in my mind if the frame of the greenhouse should be bonded to the single socket in the green house.

I would consider the frame as an extraneous part and therefore first reaction is to bond it.

But then thinking about it. bonding would reduce the risk of shock inside the greenhouse in the case of the socket became live but increase the risk of shock outside the greenhouse if the socket and greenhouse became live.

On balance I am tempted to go with not bonding, what are your thoughts?

Parents
  • But then thinking about it. bonding would reduce the risk of shock inside the greenhouse

    Not necessarily - since the 'floor' is likely to remain somewhat closer to true earth potential even when the bonded frame is at some other (possibly hazardous) potential. And not just the floor itself either - but anything metallic placed on or on it - from metal plant supports to aluminium staging.

    I wouldn't make any assumptions about the joints in the frame either - oxidized aluminium isn't the best of conductors and if the frame is factory painted/powder coated (as is increasingly popular these days) there's even less chance of a good metal-to-metal bond.

    Personally I would try to deem that a greenhouse is not a proper building and refer to the new words in 411.3.1.2.

       - Andy.

  • I would not recommend a metalclad socket in a greenhouse. It will rust and deteriorate. Also it is not suitable for the humid and damp greenhouse conditions. It may get sprayed with water. A plastic outdoor socket is better suited to this location.

    705.512.2

    522.3

    And no, I would not bond the greenhouse frame.

    Z.

Reply
  • I would not recommend a metalclad socket in a greenhouse. It will rust and deteriorate. Also it is not suitable for the humid and damp greenhouse conditions. It may get sprayed with water. A plastic outdoor socket is better suited to this location.

    705.512.2

    522.3

    And no, I would not bond the greenhouse frame.

    Z.