I'm working on an installation in a new shed at the moment. The incoming cables are 95mm single aluminum armored from a 250A MCCB with vigi. The cables will be glanded into an aluminium plate and run through ducting underground with around a 50m run. My question is.....
Am I ok using the aluminium armoring as my main earth or do I need to run in a separate earth?
I have seen some reports saying not to use the armoring as earth in singles and to only earth one end of the armoring because of circulating currents, but as these cables are aluminium armored they are non-magnetic so I don't believe circulating currents should be a problem
Any help and guidance will be very much appreciated