This time we feature the Lesser Spotted Consumer Unit. Do you notice anything strange about it children?

   

Parents
  • In addition to the use of meter tail in the box it looks as if there is a suspiciously thin red and black going to the middle 32A MCB.

  • Think that is the end of a cable behind Mike, possibly without a cpc. That MCB, along with the right hand one, looks empty, and probably held the flying 6mm cables.

    I am pretty sure the neutral "meter tail" into the neutral bar has had a haircut. Shame really, there is a perfectly good neutral bar at top left with a clamp for larger conductors, and marked N, which has been ignored

Reply
  • Think that is the end of a cable behind Mike, possibly without a cpc. That MCB, along with the right hand one, looks empty, and probably held the flying 6mm cables.

    I am pretty sure the neutral "meter tail" into the neutral bar has had a haircut. Shame really, there is a perfectly good neutral bar at top left with a clamp for larger conductors, and marked N, which has been ignored