Circuits within a caravan

Hi everyone...

What electrical testing (if any) need to be done WITHIN a caravan

Section 721 covers caravans  But, I cant find anything saying that the internal installation needs to be tested

Anyone any ideas??

Parents
  • You can certainly carry out your inspection and the dead tests.

    And some live tests too - e.g. RCD operation. If the caravan circuits are well designed they should be safe for a very wide range of supply characteristics. Remember that testing is less about verifying that the installation complies with the regs directly, as verifying that it complies with the design and is free (AFARP) from installation defects. Readings should be considered within the context of the supply in use at the time - e.g. getting a Zs reading of 100Ω when connected to a TT supply with a 'Ze' of 99.9Ω is probably acceptable, while getting a 5Ω reading with a TN-S supply with 'Ze' of say 0.5Ω probably indicates some serious problem.

      - Andy.

Reply
  • You can certainly carry out your inspection and the dead tests.

    And some live tests too - e.g. RCD operation. If the caravan circuits are well designed they should be safe for a very wide range of supply characteristics. Remember that testing is less about verifying that the installation complies with the regs directly, as verifying that it complies with the design and is free (AFARP) from installation defects. Readings should be considered within the context of the supply in use at the time - e.g. getting a Zs reading of 100Ω when connected to a TT supply with a 'Ze' of 99.9Ω is probably acceptable, while getting a 5Ω reading with a TN-S supply with 'Ze' of say 0.5Ω probably indicates some serious problem.

      - Andy.

Children
  • And some live tests too - e.g. RCD operation.

    The 9th Edition (2022) of IET Guidance Note 3 Inspection and Testing illustrates (Figure 2.37) a test method for testing 30 mA RCDs in caravans, which avoids unwanted tripping of an RCD protecting the socket-outlet to which the caravan connects.

  • If it's the illustration i think it is it's also handy for testing cascading rcd's as well.( i know not fully compliant) e.g i had a supply to a garage the other day on an EICR where there was an rcd in the house protecting the supply cable and an rcd in the garage board. 

    Gary

  • If it's the illustration i think it is it's also handy for testing cascading rcd's as well.( i know not fully compliant)

    There are illustrations for the general installation case, as there are other occasions where sending residual current back down the protective conductor might cause erroneous readings etc. (e.g. with small generators, say 5 kVA or less, or where protective conductor currents might affect the test).

    However, I can see that some configurations of domestic prosumer's electrical installations (PEIs) may need cascaded RCDs.

    The 'not fully compliant' statement (presumably regarding selectivity?) is potentially a moot point, because it is, of course, mandated by BS 7671 in certain circumstances - caravan connection socket-outlet and within the caravan itself being a good example.

  • Yes i was referring to selectivity, and in this particular case not an issue, or likely to. 

    Gary