RCD for use with DC leakage
Proposed installation of EV charge point with two socket outlets on same charger. Manufacturer claims maximum DC leakage current no more than 6mA from charger.
Installation is a small hill farm with multiple armoured submains to outbuildings. Whole site is TT earthing system with an existing 100mA (s) Type A RCD main switch.
One outbuilding has 4kW Solar PV with inverter no simple separation manufacturer claims maximum DC leakage current no more than 6mA.
With the addition of an EV charge point to an existing submain on a remote building there is the possibility of EV leakage 6mA + PV leakage 6mA =12mA of DC leakage current which may blind the RCD main switch. I have tried to locate a 100A single phase time delayed type B RCD suitable for operation by an ordinary person but have failed however I have found a Schneider A9R35291 100A 300mA  (s) type A super immunized which is suitable for use with DC currents up to 60mA.
The Schneider information says it has proposed another possibility with the use of this product and does fit with my installation requirements.
I'm not sure where I stand when the wording says proposed another possibility.
  • Well if they quote an non blinding up to 60mA., then  you are quids in as they say.  Put that RCD at the origin ,and make a note of the guaranteed DC immunity on the installation certs or some smart alec will try and find it non complaint later. (and maybe in sharpie on the incoming board as well if it is that sort of site where paper gets lost.)
    The EV will presumably either include or need its own closer protection 30mA, but that can be anything that can stand the 6mA.
  • I guess another option (provided you consider each 6mA only to occur after a fault, rather than in ordinary operating conditions) is an A-type upstream together with an RDC-DD. (Not sure if the regs have let that approach escape from 722 yet, but the physics is surely the same.)
  • I don’t know about “being quids in” as it’s going to cost the customer at least a couple of hundred quid.
  • I was under the impression that the DC leakage happens under normal operating conditions and it is only when the leakage exceeds 6mA that the internal RDC-DD operates to stop blinding of an upstream RCD.
  • The EV charger has a RDC-DD to limit leakage to 6mA and also has a 30mA RCD to BS EN 61008.
  • £199.95+VAT to be exact but a lot less than a type B which I can't find in 100A time delayed format.
    We debated that a while ago - and I think didn't come to a complete conclusion. Certainly it's easy to see how larger d.c. residual currents can occur during some simple faults (e.g. shorts between power and pilot conductors in the EV lead), it's less clear how we'd get d.c. residual currents in normal operating conductions - e.g. the 'leakage' due to capacitors (e.g. noise filters) that we're familiar with on a.c. systems presumably wouldn't pass much in the way of (pure) d.c. (I suspect we'll end up replaying the debate from last century about direct current vs continuous current, i.e. where currents vary cyclically over time but not to the extent of reversing polarity). If anyone has any definite knowledge of the d.c. leakage characteristics of EV chargers in ordinary operation, I'd be very interested...