Does This Comply?

Location: Loft.

Accessibility: Difficult.

Junction box made out of a double pattress and a blanking plate. All plastic.

Internal joints inaccessible.

Thoughts?

Z.

Parents
  • I don't see a problem with the box itself although there is obviously nothing to stop the cables getting pulled out if somebody tripped over them as they aren't clipped properly and there won't be any cable clamps in there. 

    Gary

Reply
  • I don't see a problem with the box itself although there is obviously nothing to stop the cables getting pulled out if somebody tripped over them as they aren't clipped properly and there won't be any cable clamps in there. 

    Gary

Children
  • Nobody will be walking there Gary as the loft headroom is about 500mm and tucked out of the way. The box is not on a walk way.

    Z.