Bonding industrial buildings

Bonding question 

Our main 2000a dis board is 150meters away from the main incoming water supply .. We presently have a 50mm bonding cable going to a 25mm water incoming supply is this acceptable?..

Also our gas is 15meters away from main dis board . presently has a 50mm bonding going the gas 5" incomer is this acceptable ? in 2016 it had a code C2 put on it during a eicr im about to do a new eicr and just wanted to check as struggling to find much in the regs book about gas about 28mm

Parents
  • It would be interesting to know what the C2 detected - on the face of it 50mm² copper main bond would be fine BS 7671's requirements for any earthing system (meeting both 544.1.1's 25mm² cap for non-PME systems and table 54.8's 50mm² for PME).

    There was some confusion a few years ago with a belief that bonding conductors should be under a certain overall resistance (0.1Ω or 0.05Ω) - but that was never a BS 7671 requirement - simply a rule of thumb whereby test results could be deemed acceptable without needing further calculation. Higher readings shouldn't be treated as a fail, just involve some calculation to verify that it's reasonable for the length and c.s.a. of the conductor involved.

    Or the C2 might refer inappropriate connections (typical BS 951 clamps might struggle with a 5" pipe).

       - Andy.

  • So, (in the style of Ghostbusters) What you gonna use?

    Z.

Reply Children
  • Proper pipe clamps exist, based on the exhaust clamp/ U bolt design.,.

     That is a Furse3909TB_clamp for example
    On steel pipes and building steels,  you may consider  a welded boss onto a suitable pipe flange or bracket.


    and or straps sometimes flat band is used, much like a lighting conductor,  as it can be formed into shapes that a round cable cannot.

    On smaller sizes though something like the BS951 on steroids do exist (larger pipe clamps)  OK for PSSC of a few KA.
    Mike.