Bonding industrial buildings

Bonding question 

Our main 2000a dis board is 150meters away from the main incoming water supply .. We presently have a 50mm bonding cable going to a 25mm water incoming supply is this acceptable?..

Also our gas is 15meters away from main dis board . presently has a 50mm bonding going the gas 5" incomer is this acceptable ? in 2016 it had a code C2 put on it during a eicr im about to do a new eicr and just wanted to check as struggling to find much in the regs book about gas about 28mm

Parents
  • If you want to go there Zoomup, what is the current rating of a BS951 clamp? For big pipes you can always put several in series quite easily, but will it withstand say 2000A for 5 seconds? Realistically this is as imaginary as Ghostbusters!

  • Just weld on a spur to the pipe for attaching a bonding clamp or two.

    Or just split the cables to more manageable sizes as per photo.

    Z.

  • nah Weld or braze on one M16 or M20  stud -parallel conductors may not share fault currents well.

    A 50mm  cable is not that unwieldy.
    Mike

Reply
  • nah Weld or braze on one M16 or M20  stud -parallel conductors may not share fault currents well.

    A 50mm  cable is not that unwieldy.
    Mike