I came upon this installation today. There is no P.M.E. earth terminal but just a TT rod outside. Ze is about 15 Ohms. But even accounting for the rain recently I can not see that a single 4ft. rod can achieve that low a Ze. The old Denso tape covered iron gas pipe runs underground to the road. It is bonded inside the house as is (presumably) the water pipe. The house is a 1930s aged property. I am noy happy about the final circuits in the consumer unit that do not have R.C.D. protection. Some of these supply outside metal lights on the bungalow wall. I can't imaging in the 80s or 90s this arrangement ever complying. Is the installation relying on the old gas pipe as an earth electrode? I could not do a thorough test today as the gas man was servicing the gas boiler.
Comments please?