connect boiler and nest heatlink from the same switched fused spur

My boiler is currently powered by a switched fused spur. The spur is located 40cm underneath the boiler.
I haven't checked but it is probably a 3A fuse.
My boiler is

a Ideal Logic combi ESP1 35 : idealheating.com/.../logic-combi-esp1-installation-and-servicing.pdf

I would like to add a Nest thermostat using the opentherm wiring as described here page 24: https://nest.com/support/images/misc-nest-thermostat-eu/gen3-install/3rd-gen-Nest-Learning-Thermostat-Install-Guide-UK.pdf

The wiring is relatively easy, I just need 230V AC  N + L to power the device and then 2 low voltage wires to the Opentherm on the boiler.

My question is, where do I get the the 230V AC  N + L from ? the easiest way and following the regulation.

Can I get it from the current switched fused spur that powers the boiler ?
if yes, shall I connect the nest heatlink N+L directly from the switched fused spur (load side)   

or 

shall I connect the nest heatlink N+L  directly from the boiler on the MAIN input?

Thanks in advance.

Parents
  • 1.5mm2 x 2 (no earth needed apparently if I don’t the t1/t2 on the nest.)

    Depends a bit on your chosen wiring system - typically 1.0mm² solid core or 0.75mm² flex - 1.5mm² solid core is a bit stiff to terminate into many PCB type terminals. It's usual to include an earth (c.p.c.) to all points and accessories even if it's not needed initially - to allow for a future replacement requiring an earth (actually a regs requirement in most situations).

       - Andy.

  • Thank you Andy, 0.75mm2 2+earth flex for the power, what about the cable for the low voltage  opentherm connection? Any regulations on that ? Can i use the same  0.75mm2 2+earth flex and not using the earth obviously ? Does the wire colour matter from a regulation perspective ?

Reply
  • Thank you Andy, 0.75mm2 2+earth flex for the power, what about the cable for the low voltage  opentherm connection? Any regulations on that ? Can i use the same  0.75mm2 2+earth flex and not using the earth obviously ? Does the wire colour matter from a regulation perspective ?