Single pole breakers 3 phase trunking and shared neutral

Hi, 

I have a question regarding the use of single pole MCBs on lighting trunking systems.

The idea is that the trunking system contains 8 conductors, used as follows:

L1, L2, L3, N, E (supply one - grid) 

L1, N, E (supply two - central battery for emergency lighting)

The central battery supplies lighting during an outage (AC during normal operation, DC during grid failure). This aspect is fine. 

What the customer wants is to avoid a single point of failure. Preciously, on the maintained or grid supply, L1, L2 and L3 were connected to and protected by a 3 pole MCB (across 3 phases) with a shared neutral. Moving forward, the customer has queried using single pole MCBs to protect each of the phases (split across 3 phases) and a shared neutral, thus meaning if a single MCB trips, the other 2 circuits will remain live. 

I don’t see anything wrong with this, in fact, the same result would be apparent if fuses were used. The reason I raise the question is for the purposes of isolation; when using a 3 pole MCB, a single switch can isolate an entire track however when using single pole MCBs, there are then in essence multiple points of isolation. 

Am I right in thinking that single pole MCBs can be used with a single/shared neutral, as long as the line conductors are split between 3 phases and there is appropriate labelling at all connection points for “isolation at multiple locations”? 

Thanks. 

Parents Reply Children
  • I struggle to see how, if you have 3 separate fuses feeding a busbar system, they will share the same neutral conductor (this is a typical and normal setup). The same principle would apply if the fuses were replaced with MCBs surely?

    As long as the MCBs are split across 3 phases, the neutral cannot be overloaded, again the same principle of feeding any system with fuses which can all operate independently.