Overall Diversity in huge commercial kitchen

Good afternoon

If anyone has any knowledge or gut feeling please go on and share it with me

We a well known restaurant/pub that is expected to be busy

There is a good 300A of installed power in the kitchen only

Unfortunately the power supply for the whole installation (including mechanical loads, front of house, bar, back of house etc) is a frugal 315A

So, taking into consideration that kitchen is the heart and sould of the place what do you think should be a realistic diversity to be applied on this 300A of connected load?

My initial thoughts were 50% bringing it down to 150A of constant current

However an older and much more experienced engineer proposed something along the 75% mark.

Does anyone have any similar real life experience with this?

Any insights are highly appreciated

Cheers

Parents
  • My feeling is that you need to ask a chef rather than an engineer.

    The fridges and freezers will be switched on 24/7, but the compressors will be cycling on and off so some diversity there. The exact amount would depend upon the insulation, how often the doors are opened, etc.

    The kitchen will be busy with prep when the place is closed, so low usage then front of house. Food mixers will be used intermittently and presumably mainly during prep. Microwaves will be intermittent.

    Some services may be busier than others. The chefs will not be standing idle, but some of the appliances will some of the time.

    It's not as if the whole place will be heavily loaded for a prolonged period - I would expect that the peak of activity would not be more than 2 hours - 19:30 to 21:30.

Reply
  • My feeling is that you need to ask a chef rather than an engineer.

    The fridges and freezers will be switched on 24/7, but the compressors will be cycling on and off so some diversity there. The exact amount would depend upon the insulation, how often the doors are opened, etc.

    The kitchen will be busy with prep when the place is closed, so low usage then front of house. Food mixers will be used intermittently and presumably mainly during prep. Microwaves will be intermittent.

    Some services may be busier than others. The chefs will not be standing idle, but some of the appliances will some of the time.

    It's not as if the whole place will be heavily loaded for a prolonged period - I would expect that the peak of activity would not be more than 2 hours - 19:30 to 21:30.