Overall Diversity in huge commercial kitchen

Good afternoon

If anyone has any knowledge or gut feeling please go on and share it with me

We a well known restaurant/pub that is expected to be busy

There is a good 300A of installed power in the kitchen only

Unfortunately the power supply for the whole installation (including mechanical loads, front of house, bar, back of house etc) is a frugal 315A

So, taking into consideration that kitchen is the heart and sould of the place what do you think should be a realistic diversity to be applied on this 300A of connected load?

My initial thoughts were 50% bringing it down to 150A of constant current

However an older and much more experienced engineer proposed something along the 75% mark.

Does anyone have any similar real life experience with this?

Any insights are highly appreciated

Cheers

Parents
  • I presume this is a new design. Otherwise you can see by installing a temporary data logger and get the full view. Normally 66% diversity on this kind of load is a generous figure, because of the way equipment is actually used. For example one would expect an oven to be heated once and then left at temperature during service, and pot heating used intermittently. Grills will only be on some of the time etc. I assume this is spread across a 3ph 100A supply, so a little juggling to get a reasonable spread should be quite adequate.

Reply
  • I presume this is a new design. Otherwise you can see by installing a temporary data logger and get the full view. Normally 66% diversity on this kind of load is a generous figure, because of the way equipment is actually used. For example one would expect an oven to be heated once and then left at temperature during service, and pot heating used intermittently. Grills will only be on some of the time etc. I assume this is spread across a 3ph 100A supply, so a little juggling to get a reasonable spread should be quite adequate.