EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  • I believe the guidance in the code of practice says lack of rcd and supplementary bonding is a C2. There is a recent post on here where somebody didn't follow it re a balcony socket and failed an NIC inspection. I presume the switch is in the bathroom and is mains. (i don't think we are allowed to use common sense any more)

    Gary

Reply
  • I believe the guidance in the code of practice says lack of rcd and supplementary bonding is a C2. There is a recent post on here where somebody didn't follow it re a balcony socket and failed an NIC inspection. I presume the switch is in the bathroom and is mains. (i don't think we are allowed to use common sense any more)

    Gary

Children
  • is it customary for inspector to make the assumption of absence of supplemental bonding on the basis of visual inspection alone? I don’t know for sure whether there is supplemental bonding in the flat. 

    Also if there is indeed no supplemental bonding, could there be reasons why this may be permitted in the first place - what I see in the report is something along the line - presence of supplemental bonding xxxx unless otherwise xxx)? This point was marked as present in the case of my friend’s flat in the same development - also by NICIE accredited engineer.

    Thanks