EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  • Perhaps you might like to post a link to the actual report supplied, that would be most interesting, or if you don't want to do that a copy to me at davezawadi(at)yahoo.co.uk, it would be seen by some of the right people. Looking at the pictures, it looks pretty much like a contractor job at build time, since then there have been some changes to the regulations, but it is very unlikely there is much wrong as it will be the same for all the flats.

    I am interested that the management do not want to follow this up, as I personally consider this EICR inadequate as I have said above. If the same is happening to all the owners it certainly needs attention.

    I am interested particularly in the measurements results sheet and tick list of the report. I expect that you were not present when the work was done, but I would also like to know what other inspections were carried out, particularly of the tightness of all connections, as I suspect this was way too much trouble for this Inspector.

    You have verified that the lighting is ELV, so the C2 provided was false, as the non-compliance with 701 as I noted above.

Reply
  • Perhaps you might like to post a link to the actual report supplied, that would be most interesting, or if you don't want to do that a copy to me at davezawadi(at)yahoo.co.uk, it would be seen by some of the right people. Looking at the pictures, it looks pretty much like a contractor job at build time, since then there have been some changes to the regulations, but it is very unlikely there is much wrong as it will be the same for all the flats.

    I am interested that the management do not want to follow this up, as I personally consider this EICR inadequate as I have said above. If the same is happening to all the owners it certainly needs attention.

    I am interested particularly in the measurements results sheet and tick list of the report. I expect that you were not present when the work was done, but I would also like to know what other inspections were carried out, particularly of the tightness of all connections, as I suspect this was way too much trouble for this Inspector.

    You have verified that the lighting is ELV, so the C2 provided was false, as the non-compliance with 701 as I noted above.

Children
  • Hi David, thanks for your comment. In fact, I have notified my Management Office about the RCD finding and they are in the midst of talking to the in/house engineer as it seems quite onerous that all the settings of the bathroom in my development needs upgrading to be safe for occupation!

    I will redact the pages and post here. Thanks 

  • Part 10. No. 8. RCD for low voltage circuits serving the location. "N/A" is not consistent with the C2 later on.