The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  • Thanks Kay76 very interesting. It has all the hallmarks of being entirely made up, because many items which should be N/A are ticked, the readings from measurements are not consistent ex. Circuit 5 (R1+R2 does not match alleged cable resistances) and appears to be an incorrect Zs value for the circuit, not matching the Ze value. I wonder at the Ze and actual supply arrangement too, where is your electricity meter? Do you pay the management company or the distributor directly?

    Regards

    David CEng etc.

Reply
  • Thanks Kay76 very interesting. It has all the hallmarks of being entirely made up, because many items which should be N/A are ticked, the readings from measurements are not consistent ex. Circuit 5 (R1+R2 does not match alleged cable resistances) and appears to be an incorrect Zs value for the circuit, not matching the Ze value. I wonder at the Ze and actual supply arrangement too, where is your electricity meter? Do you pay the management company or the distributor directly?

    Regards

    David CEng etc.

Children
No Data