Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  • Just a few observations from me;

    page 2-Next inspection-1 month

    this really winds me up. If all remedials are done, the report should give a reasonable time until next inspection. As it stands, another report is needed after the remedials are done

    page 3

    Agreed limitions- Agreed with no-one

    Supply protective device is a switch

    other sources of supply on page 7, which says N/A

    prospective fault current 949kA is HUGE

    rating/setting of device should be N/A as it is not settable

    page 4

    item 4.2 no mention elsewhere of loose CU

    item 4.4 should be C3, plastic CU

    item 4.15 should be N/A-plastic CU

    item 4.16 should be N/A- not required for fault protection, not TT and Zs within limits all circuits

    item 4.17 this is ticked but has given a C2 for no RCD in bathroom

    page 5

    item 5.11 e) shouldn't be N/A, should have a code

    item 6.1 b) ticked, but bedroom light not working?

    list of luminaires page 8, which says N/A so none inspected despite saying 20% in extent of sampling on page 3

    item 7.7 all N/A-should include those in bathroom

    item 8.1 a) says N/A, but has given C2 for this elsewhere

    item 8.2 says N/A but lights are ELV

    Note-his name hasn't been redacted at the bottom

    page 6

    live/live insulation resistance tests- should be N/A unless all loads disconnected. Lim on lighting circuit, "no access to spotlight connections" (page 3) , are all lights spotlights?

  • Pretty good OM, there are quite a lot more given enough time!

  • You can see I gave up near the end Slight smile