EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  • I wonder if the eagle eyed have noticed something else? The incomer appears to be 3 core SWA (old colours) but where is the armour (see 5.16 on form)? This suggests that there is a central position with all the meters, and presumably the position of all the extraneous parts bonding (if any) and an easily accessed fuse whose rating is unlikely to be the 100A stated, providing protection of the submain which he says is 16mm2 (main Earth conductor, thus undersized! Now the hard question, would I expect this to be present within the flat too, as there is one 10mm2 in the CU Earth bar as far as I can see? How was this inspected because I would expect at least a note about it. The flat heating is also interesting, perhaps central, perhaps gas, or perhaps just a single heater or perhaps that is an immersion water heater? Then there are all the ticks on metering equipment and bonding all being present and the correct size, interesting. Yet he complains that the bathroom bonding cannot be verified!

    This is definitely an inadequate EICR, with all the paperwork from a scheme. I wonder about the qualifications of the QS and the Inspector. It needs to be taken much further.

Reply
  • I wonder if the eagle eyed have noticed something else? The incomer appears to be 3 core SWA (old colours) but where is the armour (see 5.16 on form)? This suggests that there is a central position with all the meters, and presumably the position of all the extraneous parts bonding (if any) and an easily accessed fuse whose rating is unlikely to be the 100A stated, providing protection of the submain which he says is 16mm2 (main Earth conductor, thus undersized! Now the hard question, would I expect this to be present within the flat too, as there is one 10mm2 in the CU Earth bar as far as I can see? How was this inspected because I would expect at least a note about it. The flat heating is also interesting, perhaps central, perhaps gas, or perhaps just a single heater or perhaps that is an immersion water heater? Then there are all the ticks on metering equipment and bonding all being present and the correct size, interesting. Yet he complains that the bathroom bonding cannot be verified!

    This is definitely an inadequate EICR, with all the paperwork from a scheme. I wonder about the qualifications of the QS and the Inspector. It needs to be taken much further.

Children
  • the heating is centrally provided - we receive something called CHP bill based on a meter in the flat.

  • The inspector and the reviewer were two different persons - the reviewer said he was registered with NICIE (I spoke to both and both gave the same answer though the inspector sounded a bit more shaky on his findings when I queried more but he always referred me back to his boss (the reviewer).

    How this all came about was the inspector told my tenant that there were huge issues with the flat and need to install a new consumer replacement unit plus supplemental bonding (maybe he wasn't clear I don't know) which caused me to panic and reached out to him finding out more (as none of my friends in the development were ever told this).

    Actually, this flat is my home (I let it out because I'm not in the UK at the moment) . I love it to bits and won't want to risk anything for my tenant's safety. But this "inconsistent" EICR inspection is driving me nuts - I'm worried that there may be risk of fines if I don't get C2s repaired within the 28-day time bar, and it is not fair/easy to get my tenant to take leave to stay in for engineers' quotation/repair visits. With this in mind, my priority is to get "real" C2s fixed immediately and other C3s addressed when it is more convenient for my tenant. But this EICR inspector doesn't make it easy to decipher what are real and what are not .A big headache now!

  • Yes Kay76, I didn't explain that the "Schemes" (NICEIC is one) have what is called a "Qualified Supervisor", the reviewer as you have been told. In principle he is entirely responsible for the report, and is supposed to check it thoroughly, obviously he has not as you can see from the many comments above. The Inspector should have the Inspection and Test qualification C&G 2391 (or a few previous manifestations of a similar thing) but in practice may have NO qualifications at all. However the QS is fully responsible for the report, and for the very difficult job of supervising a possibly unqualified person doing what is a very skilled job without actually being present on site!

    You may care to compare this with your car Garage. The mechanic who works on your car will probably have a series of qualifications from C&G and may have them from the car manufacturer too, or may be an apprentice who will be supervised by another mechanic. However the MOT inspector will be personally qualified by the DOT, not the Garage or business although these too have approvals. If your MOT proves defective there is a simple route via the DOT to complain and get correction. This path for EICRs is very difficult via the Schemes, they have a great deal less interest than their names and alleged responsibilities suggest.

    If you find this slightly horrifying then please contact your MP, currently the Government is reviewing the situation.

    In the Engineering profession as a whole there is also a next level up so to speak, with codes of conduct and sanctions if necessary, and that is carried out by the Engineering Council, a statutory body. You will see the post nominals CEng for Chartered Engineers and IEng for Incorporated Engineers under their control and rules.

  • But this "inconsistent" EICR inspection is driving me nuts - I'm worried that there may be risk of fines if I don't get C2s repaired within the 28-day time bar, and it is not fair/easy to get my tenant to take leave to stay in for engineers' quotation/repair visits.

    Mike has set out the options and the rough costs.

    You do not need to get another inspection - all you have to do is provide evidence to the Local Authority that the C3s have been remedied.

    Or you can dig your heels in and go to NICEIC, who may do nothing, or do something slowly. I doubt that the LA would impose a penalty, but you could appeal that; but then you would need evidence that the report is inadequate. All of this whilst you are overseas.

    I'd wait a bit for NICEICs response. Then I'd probably swallow hard and get the remedial work done. It is the best of a bad job and you have my sympathy.

  • You do not need to get another inspection - all you have to do is provide evidence to the Local Authority that the C3s have been remedied.

    Next retest date is 1 month. So the report is useless for compliance with PRS legislation.

     NICEIC complaints procedure requires a complaint to be made first to the contractor

  • My apologies, that should have been "C2s" rather than "C3s".

    I don't think that the 1 month re-rest recommendation has any bearing on the legislative requirement.

  • (2) For the purposes of sub-paragraph (1)(b) “at regular intervals” means—

    (a)at intervals of no more than 5 years; or

    (b)where the most recent report under sub-paragraph (3)(a) requires such inspection and testing to be at intervals of less than 5 years, at the intervals specified in that report.

  • Sorry to clarify - do I submit the report to NiCie and ask them for a second opinion on the arbitrary bathroom Zonal system applied and visual inspection on the supplemental bonding or just state facts and get their views without naming the engineer and the report?Do I need to raise the point re 1 month interval also. Thanks

  • Is getting the RCD protection for bathroom lighting a fairly straightforward job? I’m now slightly worried that if I get another “not so competent” contractor (as I cannot discern one from another), the wiring /installation will be messed up and I will have more risks in the future! Is this a remote possibility based on experience? Thanks

  • Does it mean the report is invalid? Do I need to get another one? Thanks