EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  • There is a RCD option that has not been discussed, so long as the incoming supply is fused at 80-amps or less move the 30 mA RCD across to replace the main switch and just use one busbar.

    Then Bob’s your Uncle and Fannie’s your Aunt; and all your problems regards RCD protection for cables concealed in walls and such like that have been missed off the EICR go away, leaving two RCD related observations, a recommendation to subdivide the installation and to upgrade to a Type A RCD.

    I did something very similar in a flat for a family member who wanted to rent it out, the was a main switch consumer unit with the only RCD protection for around fifteen circuits being a RCBO on the socket circuit, the CU has a steel enclosure and is perfectly serviceable, so I swapped the main switch for a 30 mA RCD and the RCBO for a MCB, knowing if there were RCD tripping issues I would be the person getting phone calls late at night or weekends.

  • Thanks - is this an easy task for the electrician? Sorry may be asking for the obvious but I really have no clue:)