EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  •   

    Just get the lighting circuit moved onto the RCD side of the consumer unit and replace the two lights, insist on being supplied with an Electrical Minor Works Certificate to keep with the original EICR to show the required remedial work has been carried out.

    Ideally the lights would be on a separate RCD, but just go for the easy option. RCBOs for these particular consumer units are expensive and not readily available.

    Budget £100.

  • Thanks for the advice!

  • Can getting new RCD fitted into the box be done in 2 hours? Someone quoted me £200 for that (not sure with or without parts or vat - still awaiting for confirmation) - this is done through some portal matching tradesmen with clients (as I don’t have any contacts).. Thanks

Reply
  • Can getting new RCD fitted into the box be done in 2 hours? Someone quoted me £200 for that (not sure with or without parts or vat - still awaiting for confirmation) - this is done through some portal matching tradesmen with clients (as I don’t have any contacts).. Thanks