EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  • If you want proof of my previous comments, 15 minutes is all you need to know, and a new CU too!

    As to time, a 3 bed EICR takes about 2 hours on average, and I am very experienced with this. I see the line which is also a serious red flag, Sampling 20%!!! I would say this, even in 15 minutes, is simply not possible, checking all the clamping screws would take most of my time with wander-lead Earth loop testing being next longest, usually due to light fittings or ceiling roses being uncooperative. It is often quite surprising how many loose screws are present in a 1970s to 2000 installations, this may be conductor creep but I think it is probably that they were never very tight, and tiny movements over many years have had their effect.

    Someone is about to say that I don't need to check all the screws, OK you may not, but it is to make life easier that we have these "inspection free" junction boxes to hide under the floor! Larger premises are much more time consuming, and sampling may be OK, but should be cancelled immediately a defect is found in the sample, the standard QA procedure in most industries that matter.

    What to do now Kay:

    Please send copies of the unredacted documents to the Chairman of WRPC at the IET. These will be shared with the Government department currently working on the Building Regulations.

    Please write to the NICEIC and Electrical Safety First, enclosing copies of your report (unredacted) and ask for an explanation of it, at the same time referencing this thread in the forum, pointing out that Inspection of Contractors, Competence, and Safety appear to be the last of their interests.

    Please report any outcomes to the Chair, WRPC at the IET (They should probably not be published here at this stage).

    Kind regards

    David CEng etc.

Reply
  • If you want proof of my previous comments, 15 minutes is all you need to know, and a new CU too!

    As to time, a 3 bed EICR takes about 2 hours on average, and I am very experienced with this. I see the line which is also a serious red flag, Sampling 20%!!! I would say this, even in 15 minutes, is simply not possible, checking all the clamping screws would take most of my time with wander-lead Earth loop testing being next longest, usually due to light fittings or ceiling roses being uncooperative. It is often quite surprising how many loose screws are present in a 1970s to 2000 installations, this may be conductor creep but I think it is probably that they were never very tight, and tiny movements over many years have had their effect.

    Someone is about to say that I don't need to check all the screws, OK you may not, but it is to make life easier that we have these "inspection free" junction boxes to hide under the floor! Larger premises are much more time consuming, and sampling may be OK, but should be cancelled immediately a defect is found in the sample, the standard QA procedure in most industries that matter.

    What to do now Kay:

    Please send copies of the unredacted documents to the Chairman of WRPC at the IET. These will be shared with the Government department currently working on the Building Regulations.

    Please write to the NICEIC and Electrical Safety First, enclosing copies of your report (unredacted) and ask for an explanation of it, at the same time referencing this thread in the forum, pointing out that Inspection of Contractors, Competence, and Safety appear to be the last of their interests.

    Please report any outcomes to the Chair, WRPC at the IET (They should probably not be published here at this stage).