EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  • Ohhh Dear!

    That is me well and truly kicked into the trash can then.

    OK I do not do EICRs/PIR as a habit, only very very infrequent.

    For a typical 3 Bed Terrace with furniture and folk about the place then I would allow 4 hours plus an hour to cover hand written report.

    I am not against sampling if it is does effectively reflect the true condition with a reasonable expected accuracy.

    My initial first inspection (quick glance) and info, if any, supplied by the householder .

    My first guess would be the householder might be pretty much correct.

    However they might be slightly mistaken.

    They might be a little bit apprehensive/embarrassed  so supply me with "a different version of the truth".

    They might actually be be extremely economical with the truth.

    So my first glance might lead me to suspect , yes this was all installed by the same entity XXX time ago and nothing/not much as changed. My further detailed inspection and opening up accessories and yes or no to sampling and any %age will be based upon that.

    If my initial first guess leads me to conclude Entity X did most of it, then entity Y added/altered YY then Entity Z added/altered ZZ then I`d probably apply those inspections in 3 possible categories.

    Then I got a feel of all that I inspect appropriately the test everything.

    Sometimes everything is pretty straightforward but often not an you get every combination under the sun but I am only happy if I have done a very reasonable I & T that is extremely likely (but not infallible) reflection of the state of the installation.

    Very often I walk away thinking "Hah I thought that might have been the case" over something I`ve discovered that has been or will be missed by others.

  • It is not how long it takes ebee, it is doing the job properly! To average a couple of hours is a process which has taken me years to achieve, but in many ways an economic necessity. If you charge a sensible price for your 4-5 hours you would not be able to be in business, a minimum of say £250, and you might just get 2 done per day if close together.

    This thread is all about a report which a kind householder has shown us. We have pointed out numerous errors etc, and then we are told it took 15 minutes and they need a new CU, which is clearly ridiculous from all points of view.

    You have seen my response, and you also know that I have been reviewing EICRs for a year or more. In fact this one is the worst I have ever seen, except some which I actually know were made up, genuine drive by's!

    You know the saying "Practice makes perfect", in EICR terms more true than you can even imagine.

  • Agreed David, like I say I very rarely do them. I have seen the 20 minute ones. In fact one firm I know near me has one QS and a few sparks doing the I & T for him, They do three a day , make notes and he does the paperwork. He wants them to do 4 a day. I have seen  a few of them by that firm and believe me I do not believe them, well they do not seem to bear much relationship to the actual installations I see before me. I have seen one of his done by himself, took him less than 30 mins and I queried if it was actually the same property I was viewing. 

    A mixture of things that were missed yet seemed obvious to me, things that were defected yet perfickly OK in my opinion.  no cpc earth bar earthing conductor supplying an electric shower yet a R1 + R2 reading from that circuit . etc etc etc. 

    I was once asked to give an estimate for remedials for a number of properties based just on the one page listing defects from each report. When I asked for each complete (NICEIC) report I was refused, so I declined, I had a very good idea just from reading the defect list just which firm had produced them.

    I advised the office requesting such to place them in "File 13" , when they asked what file 13 was I tore the sheets in half and dropped them in the bin , stating "That is file 13" . Actually I thought file 13 was common lingo  in offices. LOL

  • A bit like allocating the work to Miss Anybody.

  • I wrote to NICIE over the weekend - to clarify the basis in arriving at C2s(not formal complaint). They told me the EICR inspector need to follow the bathroom lighting guidance and told me to go back to them and ask them revise the code. If they refuse, then I can lodge a formal complaint against them. Similarly, they need to test the supplemental bonding with some prescribed method. I have gone back to the vendor who assigned them to me and requested for the same. Judging from their past reactions, they may just sit mum and do nothing but I think I will hold off from any remedial work until I hear back because I really don’t want to mess up my current installation if  nothing is wrong! 

  • We shall all be very interested to hear the outcome Kay76, please don't forget us! By the time you hear anything I suspect that this will no longer be on the first (latest) page, please start a new one or you may mail me davezawadi(at)yahoo.co.uk, if that is easier and I will do it.

    Kind regards David

Reply
  • We shall all be very interested to hear the outcome Kay76, please don't forget us! By the time you hear anything I suspect that this will no longer be on the first (latest) page, please start a new one or you may mail me davezawadi(at)yahoo.co.uk, if that is easier and I will do it.

    Kind regards David