This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

Parents
  • Fittings like these are still available and can be bought for £2.27 each including VAT.

    However add on a transformer, lamp and fire hood; and they cost more than a reasonable dedicated IP, fire and acoustic rated LED downlight that is more economical to use and is actually fit for purpose.

    These fittings were rarely fit for purpose and generally  badly installed,having said that I still have three in my bedroom in a bulkhead over the wardrobe doors, but they are mounted in such a way that the integrity of the ceiling above them is maintained. 

    These days I would not entertain fitting them in my own home or anyone else’s either for that matter.

  • Can anyone please help me with this -  the inspector now offered to move the lighting circuit to the RCD section for free (I didn’t ask for this) because they said they can’t amend the issued EICR report otherwise.  I know this is not ideal because someone had said that this could pose issues in future with lighting out when sockets are out. Can I ask whether the risk means that I will end up having to replace all lights and the wirings if sockets become faulty in future? ( Sorry if I’m asking an obvious question because I really don’t understand what are in store for me if I go down this route). Thanks for your help!

  • Just to add - the inspector didn’t want to test the supplemental bonding  hence he is offering this (via the intermediary)

  • If it gets him off your back and a "pass" for now, let him do it, there are loads  of flats and other small buildings with one RCD and the potential for the one-out all-out problem, and most of them are just fine without any tripping  problems for intervals of many years.

    It is not something to design into a new installation of course,  not best practice,  but it is not a show stopper. And it can be done  right now. (it is at most an  'improvement recommended' level of comment on any report)

    At some point in the next decade that consumer unit, or at least some of it, will probably be changed and it can all be addressed then, but that you can arrange in your time and on your terms.


    If it is not causing a problem tripping on the sockets now, it won't cause a problem in the immediate future either by adding a few lamps to the same RCD.

    Mike.

    .

  • Thanks Mike - this is really helpful! 

    to be honest, I’m a bit worried letting the guy modified things in my flat because of what happened before. Is there anything that I ought to tell my tenant to keep any eye on when they come to do the work? Thanks again!

  • If the tenant is in perhaps they can distract him with the offer of tea or coffee and then take some before and after pix  of that consumer unit with covers off while he goes to the loo ;-)

    He should use the machine that goes bing to test the RCD but at the least exercise the 'test' button before packing up.

    I reckon about 30 mins max.

    M.

  • Just a ditto on the RCD scenario. In an ideal situation you`d avoid a RCD tripping out too many circuits.

    Some years ago you didn`t have much choice, an RCD might be fitted as a "Main Switch" thereby protecting all circuits.

    Later some were taken back onto a plain "Mainswitch" (lighting for example)  and the remainder (sockets for example) on RCD.

    Later on again Dual RCDs each protecting a few MCB circuits offered the chance to just lose around half of the circuits per RCD trip situation (often called for some nonsensical reason as a "High Integrity" Board/consumer unit)

    . Then additional plain ordinary MCB circuits or a few RCBO circuits added on (and RCBO is an MCB and an RCD combined just to protect only one circuit_

    . Or you could have One plain switch and all circuits RCBO (If you were gonna call any combo "High Integrity" then surely it would be this one.

    One of our esteemed contributors did point out that with many/all RCD circuits on an installation you could have, in that installation, much leakage to earth and not be aware of it because not any one circuit would actually cause a trip, but the same could be said about the no RCD/RCBO only MCB/Fuse circuits anyway.

    There are at least two of us on this forum who are "Front Enders" (One RCD covering all circuits) and not much in the way of nuisance trips over many years, however the chances of such are many more than by splitting down to increase the number of RCDs in an installation.

    Believe me I have given the shortened version of what I wanted to explain

  • Thanks - really appreciate all the kind help on this! Hopefully this matter can be resolved ASAP! 

Reply
  • Thanks - really appreciate all the kind help on this! Hopefully this matter can be resolved ASAP! 

Children
No Data