EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

  • Is getting the RCD protection for bathroom lighting a fairly straightforward job? I’m now slightly worried that if I get another “not so competent” contractor (as I cannot discern one from another), the wiring /installation will be messed up and I will have more risks in the future! Is this a remote possibility based on experience? Thanks

  • Thanks for your suggestion

  • Does it mean the report is invalid? Do I need to get another one? Thanks 

  • Where is your property in the Country?

  • Cheap and nasty down-lights like these are the bane of electricians life’s, in my opinion they should never have been sold and installed in the first place.

    The amount of time and effort they waste whilst doing EICRs trying to justify their use is ridiculous, as is the amount of time and effort put into prolonging this discussion on this forum.

    Most people just accept they are #### and have them replaced with new modern LED IP65, fire and acoustic rated without all this ridiculous effort to prove there is nothing wrong with them.

    Skimming through the discussion I think I was the only person to raise concerns about the probable lack fire rating, they may also lack there required acoustic rating and may also be potentially causing condensation issues within the fabric of the building.

    Unless someone actually removes the lamp and has a look up into a fitting to see if it is open backed or an enclosed can and tells us what they are are we don’t really know whether issues are, if I were doing the EICR I would definitely have removed the lamps and possibly removed the fittings from the ceiling, because in addition to assessing the suitability of the fitting in general and for use in that actual location, they have halogen lamps in them and they generally melt and burn the 12 volt cables to the lamp holders and in many cases the 230 volt circuit cables and transformers as well.

    In addition the standard of installation needs to be assessed, many installers just used choc strip connectors and often failed to ensure they are enclosed and insulated as required, many put the fittings to close to timber joists and framing with some actually cutting into the timber to fit the lights, I have seen ceiling joists and the bottom chords of roof trusses completely cut out doing structural damage as well as clear and obvious fire risks.

    Neither the lamps or the transformers should be covered with insulation with fire hoods or enclosures installed as required.

    Regards that EICR, it is very lacking in so much that if I had completed it there would be a lot more observations and codes to what is on that one.

    napitweb.azureedge.net/.../CP 1 07 P 24-25 Downlighters.pdf

  • Thanks - not sure I really understand what needs to be done beyond replacing the lights. Do you mind letting me know what could be things to look out for when I get another workman in?

    Between, I am aware our management office did a very thorough fire and electrical installation review for all the buildings/flats in the development following the Greenfeld incident. Nothing came up on bathroom lighting from the review but  on the safe side I notified my management office few days ago to get them to look into this lighting/RCD/ supplemental bonding matter (because the installation in my flat hasn’t been altered and if there is significant issue on mine, they need to make sure the other flat owners are aware and address them as well) but they haven’t come back to me yet. Hopefully will have better idea when they come back 

  •   

    Just get the lighting circuit moved onto the RCD side of the consumer unit and replace the two lights, insist on being supplied with an Electrical Minor Works Certificate to keep with the original EICR to show the required remedial work has been carried out.

    Ideally the lights would be on a separate RCD, but just go for the easy option. RCBOs for these particular consumer units are expensive and not readily available.

    Budget £100.

  • Thanks for the advice!

  • There is a RCD option that has not been discussed, so long as the incoming supply is fused at 80-amps or less move the 30 mA RCD across to replace the main switch and just use one busbar.

    Then Bob’s your Uncle and Fannie’s your Aunt; and all your problems regards RCD protection for cables concealed in walls and such like that have been missed off the EICR go away, leaving two RCD related observations, a recommendation to subdivide the installation and to upgrade to a Type A RCD.

    I did something very similar in a flat for a family member who wanted to rent it out, the was a main switch consumer unit with the only RCD protection for around fifteen circuits being a RCBO on the socket circuit, the CU has a steel enclosure and is perfectly serviceable, so I swapped the main switch for a 30 mA RCD and the RCBO for a MCB, knowing if there were RCD tripping issues I would be the person getting phone calls late at night or weekends.

  • Ditto to that one Sparkingchip