EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

  • the heating is centrally provided - we receive something called CHP bill based on a meter in the flat.

  • Thanks for your comments, unfortunately I don't really understand the bulk of it :) Can anyone spot significant risks in my flat which may need further investigation?

    As far as I'm aware at least 3 flats (friends') in the same development were tested previously - all with satisfactory results and some C3 improvements like RCD box is plastic. Also, our management office did an extensive review on all the electrical installations sometime back (2020/2021 i think) and any known issues would have been fully addressed back then - no issues were flagged re standard electrical installations within our flats.

    Also - is it still worth writing in to NICIE for their second opinion re the two C2s? I am kind of lost on how to resolve this amicably. I'm not in UK and it is not easy to get my tenant to stay in for visits by engineers for quotation/remedial works etc. And both my tenant and myself do not have any knowledge on all these engineering stuffs.

  • The inspector and the reviewer were two different persons - the reviewer said he was registered with NICIE (I spoke to both and both gave the same answer though the inspector sounded a bit more shaky on his findings when I queried more but he always referred me back to his boss (the reviewer).

    How this all came about was the inspector told my tenant that there were huge issues with the flat and need to install a new consumer replacement unit plus supplemental bonding (maybe he wasn't clear I don't know) which caused me to panic and reached out to him finding out more (as none of my friends in the development were ever told this).

    Actually, this flat is my home (I let it out because I'm not in the UK at the moment) . I love it to bits and won't want to risk anything for my tenant's safety. But this "inconsistent" EICR inspection is driving me nuts - I'm worried that there may be risk of fines if I don't get C2s repaired within the 28-day time bar, and it is not fair/easy to get my tenant to take leave to stay in for engineers' quotation/repair visits. With this in mind, my priority is to get "real" C2s fixed immediately and other C3s addressed when it is more convenient for my tenant. But this EICR inspector doesn't make it easy to decipher what are real and what are not .A big headache now!

  • It does not look good - it is not uncommon for the odd mistake or three on an EICR but when you are faced with more than a few then it certainly starts to look a bit dodgy even to the less pedantic of us. I`d get onto the NICEIC in the first instance and make a port of call to whatever the old Trading Standards Office etc is called these days

  • Yes Kay76, I didn't explain that the "Schemes" (NICEIC is one) have what is called a "Qualified Supervisor", the reviewer as you have been told. In principle he is entirely responsible for the report, and is supposed to check it thoroughly, obviously he has not as you can see from the many comments above. The Inspector should have the Inspection and Test qualification C&G 2391 (or a few previous manifestations of a similar thing) but in practice may have NO qualifications at all. However the QS is fully responsible for the report, and for the very difficult job of supervising a possibly unqualified person doing what is a very skilled job without actually being present on site!

    You may care to compare this with your car Garage. The mechanic who works on your car will probably have a series of qualifications from C&G and may have them from the car manufacturer too, or may be an apprentice who will be supervised by another mechanic. However the MOT inspector will be personally qualified by the DOT, not the Garage or business although these too have approvals. If your MOT proves defective there is a simple route via the DOT to complain and get correction. This path for EICRs is very difficult via the Schemes, they have a great deal less interest than their names and alleged responsibilities suggest.

    If you find this slightly horrifying then please contact your MP, currently the Government is reviewing the situation.

    In the Engineering profession as a whole there is also a next level up so to speak, with codes of conduct and sanctions if necessary, and that is carried out by the Engineering Council, a statutory body. You will see the post nominals CEng for Chartered Engineers and IEng for Incorporated Engineers under their control and rules.

  • But this "inconsistent" EICR inspection is driving me nuts - I'm worried that there may be risk of fines if I don't get C2s repaired within the 28-day time bar, and it is not fair/easy to get my tenant to take leave to stay in for engineers' quotation/repair visits.

    Mike has set out the options and the rough costs.

    You do not need to get another inspection - all you have to do is provide evidence to the Local Authority that the C3s have been remedied.

    Or you can dig your heels in and go to NICEIC, who may do nothing, or do something slowly. I doubt that the LA would impose a penalty, but you could appeal that; but then you would need evidence that the report is inadequate. All of this whilst you are overseas.

    I'd wait a bit for NICEICs response. Then I'd probably swallow hard and get the remedial work done. It is the best of a bad job and you have my sympathy.

  • You do not need to get another inspection - all you have to do is provide evidence to the Local Authority that the C3s have been remedied.

    Next retest date is 1 month. So the report is useless for compliance with PRS legislation.

     NICEIC complaints procedure requires a complaint to be made first to the contractor

  • My apologies, that should have been "C2s" rather than "C3s".

    I don't think that the 1 month re-rest recommendation has any bearing on the legislative requirement.

  • (2) For the purposes of sub-paragraph (1)(b) “at regular intervals” means—

    (a)at intervals of no more than 5 years; or

    (b)where the most recent report under sub-paragraph (3)(a) requires such inspection and testing to be at intervals of less than 5 years, at the intervals specified in that report.

  • Sorry to clarify - do I submit the report to NiCie and ask them for a second opinion on the arbitrary bathroom Zonal system applied and visual inspection on the supplemental bonding or just state facts and get their views without naming the engineer and the report?Do I need to raise the point re 1 month interval also. Thanks