EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

  • I said earlier in the discussion that RCBOs are expensive and not readily available for this consumer unit, based on having done an Internet search.

    You would also need to get the electrician to confirm that available RCBOs are compatible.

    To be honest I don’t think it’s worth spending money on the existing consumer unit trying to partially update it, as Chris Pearson says above replace it completely or as I said swap the existing components around in it to make use of what is already there.

  • Fifteen minutes is not long enough to test and inspect the installation, if the tenant is correct.

    Something definitely does not ring true, is it possible that the electrician had tested this installation previously some years ago and already had a test certificate or there’s a schedule of test results stuck to the front of the consumer unit or he had access to a previous EICR?

  • I always like to think the best of people, but I am questioning what went on here.

    In the photo showing the socket ring continuity rest being carried out only the red live conductors are removed from their terminals, the black neutrals and the green/yellow circuit protective conductors (earth wires) are still terminated in their busbars.

    Then the test result on the tester is 0.14 ohms , but it doesn’t correspond with either of the test results recorded in the report.

    Far be it for me to cast  aspersions, but that looks like minimal testing to revalidate an existing Schedule of Test Results or even one from a flat in another part of the building.

    I will revalidate EICRs that I have done previously, knowing I have previously fully tested and inspected the installation; and I have carried out any remedial work required, but I do actually say that is what I have done on the paperwork.

  • I never had an EICR before - I commissioned him for a full EICR inspection 

  • Noted - thanks

  • I don’t know what this guy is up to - perhaps he did test other stuffs but didn’t give me photos. I think my tenant is correct because she gave me a detailed rundown on what he did - he tested the fuse board and socket in living room and then for others like bathroom and bedroom he just switched on the light and cast his eyes and said there are issues need to change CU and left (all in not more than 15 mins)

  • Well I am slow when doing EICRs and I very very rarely do them, others are a lot faster than me but I have never met anyone who is that fast ever! 15 mins is what we call a "drive by", If we are lucky then we can visual sockets, switches, light fittings, in situ. Not open up a sample of same to inspect connections etc, not test (apart from plug in the meter for 1 type of test. That`s about it but that is not an EICR, it is a quick glance, that is all.

  • If you want proof of my previous comments, 15 minutes is all you need to know, and a new CU too!

    As to time, a 3 bed EICR takes about 2 hours on average, and I am very experienced with this. I see the line which is also a serious red flag, Sampling 20%!!! I would say this, even in 15 minutes, is simply not possible, checking all the clamping screws would take most of my time with wander-lead Earth loop testing being next longest, usually due to light fittings or ceiling roses being uncooperative. It is often quite surprising how many loose screws are present in a 1970s to 2000 installations, this may be conductor creep but I think it is probably that they were never very tight, and tiny movements over many years have had their effect.

    Someone is about to say that I don't need to check all the screws, OK you may not, but it is to make life easier that we have these "inspection free" junction boxes to hide under the floor! Larger premises are much more time consuming, and sampling may be OK, but should be cancelled immediately a defect is found in the sample, the standard QA procedure in most industries that matter.

    What to do now Kay:

    Please send copies of the unredacted documents to the Chairman of WRPC at the IET. These will be shared with the Government department currently working on the Building Regulations.

    Please write to the NICEIC and Electrical Safety First, enclosing copies of your report (unredacted) and ask for an explanation of it, at the same time referencing this thread in the forum, pointing out that Inspection of Contractors, Competence, and Safety appear to be the last of their interests.

    Please report any outcomes to the Chair, WRPC at the IET (They should probably not be published here at this stage).

    Kind regards

    David CEng etc.

  • Ohhh Dear!

    That is me well and truly kicked into the trash can then.

    OK I do not do EICRs/PIR as a habit, only very very infrequent.

    For a typical 3 Bed Terrace with furniture and folk about the place then I would allow 4 hours plus an hour to cover hand written report.

    I am not against sampling if it is does effectively reflect the true condition with a reasonable expected accuracy.

    My initial first inspection (quick glance) and info, if any, supplied by the householder .

    My first guess would be the householder might be pretty much correct.

    However they might be slightly mistaken.

    They might be a little bit apprehensive/embarrassed  so supply me with "a different version of the truth".

    They might actually be be extremely economical with the truth.

    So my first glance might lead me to suspect , yes this was all installed by the same entity XXX time ago and nothing/not much as changed. My further detailed inspection and opening up accessories and yes or no to sampling and any %age will be based upon that.

    If my initial first guess leads me to conclude Entity X did most of it, then entity Y added/altered YY then Entity Z added/altered ZZ then I`d probably apply those inspections in 3 possible categories.

    Then I got a feel of all that I inspect appropriately the test everything.

    Sometimes everything is pretty straightforward but often not an you get every combination under the sun but I am only happy if I have done a very reasonable I & T that is extremely likely (but not infallible) reflection of the state of the installation.

    Very often I walk away thinking "Hah I thought that might have been the case" over something I`ve discovered that has been or will be missed by others.

  • It is not how long it takes ebee, it is doing the job properly! To average a couple of hours is a process which has taken me years to achieve, but in many ways an economic necessity. If you charge a sensible price for your 4-5 hours you would not be able to be in business, a minimum of say £250, and you might just get 2 done per day if close together.

    This thread is all about a report which a kind householder has shown us. We have pointed out numerous errors etc, and then we are told it took 15 minutes and they need a new CU, which is clearly ridiculous from all points of view.

    You have seen my response, and you also know that I have been reviewing EICRs for a year or more. In fact this one is the worst I have ever seen, except some which I actually know were made up, genuine drive by's!

    You know the saying "Practice makes perfect", in EICR terms more true than you can even imagine.