Table 4D1A

Table 4D1A has cables that when reference method F is used starting at 25mm^2, I cannot find a suitable explanation as to why 25mm^2 single insulated cables are okay to use at this CSA and not any less.

If I used 25mm^2 cable from this table the insulation is still the same as a smaller cable from the same table.

is there any justification that when the cable gets to 25mm^2 it somehow becomes acceptable to use?

Parents
  • Useful figures to pencil into the gaps in 7671 there. Thanks Lyle.

    (Like using makers data it is nearly always OK to refer to another equivalently authorative  standard on those occasions '7671 falls short... )

    Mike

Reply
  • Useful figures to pencil into the gaps in 7671 there. Thanks Lyle.

    (Like using makers data it is nearly always OK to refer to another equivalently authorative  standard on those occasions '7671 falls short... )

    Mike