SY Cabling - Current Carrying Capacity

Often I am finding SY used for the permanent fixed wiring of installations for circuits like Air Conditioning and Sockets. Apart from the obvious with SY Cable not permitted as such for these circuits as per BS 7671, Is there a specific current carrying capacity table for SY? This is because sometimes on EICR's we are finding SY being too small for the load but cannot always find the exact table/document to back this up.

Thanks

ElectricalCuriousity

Parents Reply Children
  • Was not aware of that. It would in my view be reasonable to use the current ratings supplied by the maker. De rate if required for grouping or high ambients.

  • It would in my view be reasonable to use the current ratings supplied by the maker.

    But it would have to be the specific manufacturer and product, because there is no constructional standard.

    Which is OK ... but there's a lot of the stuff out there with no apparent markings for us to check ...

  • That's not really true, The copper core areas and insulation thicknesses are set by various DIN standards and the copper CSA is to the same standard as any  similarly stranded flex without the outer braid.

    The great unknown is the sometimes rather whispy steel braid, which when earthed is very good at blowing RCDs if the cable gets damaged, but tends to lose if pitted against a hot wire fuse of more than perhaps 10A, burning back from the nail or what-ever faster than the fuse blows (a self clearing fault..). Braid coverage also varies between brands from about 85% of the outer area to something like the wire braid equivalent of fishnet tights from the shallowest  end of the market.

    The second unknown is the degree of UV resistance, but that varies among ordinary cables too, and if in doubt avoid the most exposed locations or insist it be inspected regularly.

    We use a lot of it at work for things that need screening from an EMP and to be flexible, but do not use it as an armour,

    Hence my earlier comment that it is fine as  slightly  tougher than arctic flex for similar locations, but it is nothing like an  SWA. And I agree with Broadgage - earth braid tails at both ends please, but use a CPC core as well.

    Mike